Subject: Binary IO control of TTFSS box working - can lock PDH remotely 

I've worked out how to get the binary IO to work with the TTFSS box so that we can activate switches in that unit. It wasn't working in the setup yesterday because of physics. Actually - there is a 10K pulldown resistor in the Acromag unit that attaches the output to ground. The actual circuit looks like this:

 

VCC (5V) --- (4.99K) --- T1EN -----|-----DIO0 ----(6.2V if DOUT set to 1)---- (10K) ------ | GND

.........   TTFSS...................................| ..............................ACROMAG ...............................................|

T1EN is measured by the switch-chip (SN74HCT157D, chip U3 in D040423) to determine whether it should be open or closed. We need to bring T1EN below 0.8V to get the TTL logic to work.

If DOUT is set to 1, then DIO0 and T1EN become the excitation voltage, 6.2V, and the switch circuit reads high. If DOUT is set to 0, the excitation voltage is removed and we just end up with a voltage divider and around 3.33V at T1EN - which does not register as low.

We can get around this by adding a smaller resistor, say 810 Ohms, in parallel to the 10K, to lower the effective resistance of the pull-down resistor to 750 Ohms. The maximum current the Acromag unit will have to supply is 6.2V/750 Ohms = 8.4mA.

So that's what I did. Now, when I switch DOUT to 1, I see 6.2V at T1EN and when I switch DOUT to 0, I see 0.669V at T1EN. The TTFSS box registers these as two different states and I can lock and unlock the PDH loop from EPICS.