40m QIL Cryo_Lab CTN SUS_Lab TCS_Lab OMC_Lab CRIME_Lab FEA ENG_Labs OptContFac Mariner WBEEShop
  40m Log  Not logged in ELOG logo
Entry  Tue Jan 12 08:21:47 2021, anchal, HowTo, CDS, Acromag wiring investigation SingleEndedNonFloatingWiring.pdfSingleEndedFloatingWiring.pdfDifferentialSignalWiring.pdf
    Reply  Tue Jan 12 11:42:38 2021, gautam, HowTo, CDS, Acromag wiring investigation 
       Reply  Wed Jan 13 16:09:29 2021, Anchal, HowTo, CDS, Acromag wiring investigation SimpleTestsStriptoolImages.pdf
          Reply  Tue Jan 26 12:59:51 2021, Anchal, HowTo, CDS, Acromag wiring investigation TestingDifferentialSignalWithFloatingRTNwrtIN-.pdf
             Reply  Tue Jan 26 15:37:25 2021, Anchal, HowTo, CDS, Acromag wiring investigation GeneralLabWiring.pdfGeneralLabWiring2.pdfGeneralLabWiring3.pdf
                Reply  Fri Jan 29 17:57:17 2021, Anchal, HowTo, CDS, Acromag wiring investigation GeneralLabWiringDiffWith2Wires.pdfGeneralLabWiringDiffWith3Wires.pdfDiffReadResistorbtwnINandRTN.pdf
Message ID: 15778     Entry time: Tue Jan 26 12:59:51 2021     In reply to: 15762     Reply to this: 15779
Author: Anchal 
Type: HowTo 
Category: CDS 
Subject: Acromag wiring investigation 

Taking inspiration from SR785 on how it reads differential signal, I figured that acromag too always need a way to return current through RTN ports always. That must be the reason why everything goes haywire when RTN is not connected to IN-. Now for single ended signals, we can always short RTN to IN- and keep same GND but then we need to be careful in avoiding ground loops. I'm gonna post a wiring diagram in next post to show how if two signal sources connect to each other separately, a GND loop can be formed if we tie each IN- port to RTN on an acromag.
Coming to the issue of reading a differential signal, what SR785 does is that it connects 50 Ohm resistance between Earth GND and differential signal shields (which are supposed to signal GND). In a floating GND setting, SR785 connects a 1 MOhm resistor between input shield and Earth GND. This can be used to read a differential signal through a single BNC cable since the shiled can take arbitrary voltages thanks ti the 1 MOhm resistor.

We can do the same in acromag. Instead of shorting RTN to IN- ports, we can connect them through a large resistor which would let IN- float but will give a path for current to return through RTN ports. Attached here are few scenarios where I connected IN- to RTN throguh wire, 820 Ohms, 10kOhms and 1MOhms in two sub cases where RTN was left open or was shorted to Earth GND. In all cases, the signal was produced by a 9V battery outputing roughly 8.16V. It seems that 10kOhm resistor between RTN and IN- with RTN connected to Earth GND is the best scenario noise wise. I'll post more results and a wiring diagram soon.

Attachment 1: TestingDifferentialSignalWithFloatingRTNwrtIN-.pdf  968 kB  | Hide | Hide all
TestingDifferentialSignalWithFloatingRTNwrtIN-.pdf TestingDifferentialSignalWithFloatingRTNwrtIN-.pdf TestingDifferentialSignalWithFloatingRTNwrtIN-.pdf TestingDifferentialSignalWithFloatingRTNwrtIN-.pdf TestingDifferentialSignalWithFloatingRTNwrtIN-.pdf TestingDifferentialSignalWithFloatingRTNwrtIN-.pdf TestingDifferentialSignalWithFloatingRTNwrtIN-.pdf TestingDifferentialSignalWithFloatingRTNwrtIN-.pdf